Configuration and calibration Fibaro Roller Shutter module FGRM-222.
Hi All,
First I had many problems to calibrate the module. Percentage didn?t work.
The FGRM-222 needs to be a calibration process first.
The module needs a minimum ballast of 1W or more (230V screen motor with end switches)
If you use a relay on the outputs, the calibration didn?t work.
I have a solution for this:
First 1 connect a toggle switch(1 - 0 - 2)on the outputs Q1 and Q2 from the FGRM-222.
1 to output Q1, 2 to output Q2 and the P (middle contact) connect to a 230V/20W bulb, other site of the bulb connect to N.
If I put the switch on 1 and connect S1 to L the bulb is on. Put the switch on 2 the bulb is on if I connect S2 to L
With a stopwatch I measuring the time that the screen needs to be go up and down. (For me 40s up and 40s down).
Set the switch to position2
Now I start the calibration function (Zwave options variable 29>1 didn?t work fine for me) so I use the manual option: Connect S1 3x fast to L, 3xfast to L, 3x fast to L and the calibration function will start
The bulb go on.
Start the stopwatch and put the switch in position 1 after the time is expire that the screen needs to be go up.
Now put the switch in position 2 after the time is expire that the screen needs to be go down.
After these process the FGRM-222 calibration is almost completed.
NOW FIRST: go to your device option of the FGRM-222 in the vera. (Devices>FGRM-222>Device Options)
Set the variable 18 to 0 and save this. You can check this if you select back and select device options for the 2 time. Now you will see the current value. If it?s ok? it?s 0. If it is 1 or more it is not ok? and you will be need to store the variable for the 2 time.
If it is be 0 the calibration process is completed and the FGRM-222 is ready for use. Percentage will work fine now.